After losing input power to this UPS, it now won't power on correctly again. The warning led becomes red, all others are off.
We have a management card attached and can access it. We see the warning message A power factor correction fault exists.
This prevents me from turning output power on or running a self test.
When I try to turn the UPS off and on again, it comes back to the same state, and the logs say:
21.10.2014 | 10:28:22 | UPS: A power factor correction fault exists. |
21.10.2014 | 10:27:52 | UPS: A power factor correction fault no longer exists. |
21.10.2014 | 10:27:29 | UPS: A power factor correction fault exists. |
Current input voltage seems to be normal: Input Voltage: 230.7 VAC
Status from CLI:
apc>ups -st
E000: Success
State: Off, PFC Fault
apc>detstatus -all
E000: Success
Status of UPS: Off, PFC Fault
Last Transfer: None
Input Status: Voltage too low
Runtime Remaining: 18 hr 12 min 15 sec
Battery State Of Charge: 99.9 %
Output Voltage: 0.0 VAC
Output Frequency: 0.0 Hz
Output Watts Percent: 0.0 %
Output VA Percent: 0.0 %
Output Current: 0.00 A
Output Efficiency: -- %
Output Energy: 1179.909 kWh
Input Voltage: 231.4 VAC
Input Frequency: 50.1 Hz
Battery Voltage: 124.8 VDC
Battery Temperature: 27.4 C, 81.3 F
Self-Test Result: Refused via management device due to invalid state
Self-Test Date: 10/20/2014
Calibration Result: Unknown
Calibration Date: 02/06/2014
Any idea, can we fix this quickly?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:49 AM . Last Modified: 2024-03-12 02:45 AM
Thanks for the update. Yes, this type of fault requires a replacement typically.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:49 AM . Last Modified: 2024-03-12 02:45 AM
Update: I got hold of APC support, and they will send a replacement unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:49 AM . Last Modified: 2024-03-12 02:45 AM
Thanks for the update. Yes, this type of fault requires a replacement typically.