APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:36 PM
For the most of our UPS systems we use ticket number FA164737 from the knowledge base to perform a firmware upgrade. We also have some Smart-UPS 750 RM systems with for example firmware revision 668.19.I, these kind of revision numbers can't be found in the table in the above mentioned ticket (knowledge base). Does anyone know where to find if those systems need a new firmware and also where to find those firmware files?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:36 PM
Thanks for the fast responses!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:36 PM
Hi Lisa,
Unfortunately, these would be older Smart-UPS 750 RMs and their firmware is not field upgradable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:36 PM
Lisa,
If the UPS are not included in the list then they do not have upgradeable firmware. Smart-UPS models beginning with "SMT", "SMX", "SMC", or “SRT” can be upgraded. Smart-UPS models beginning with SU, SUA, SURT, SURTD cannot be upgraded. An easy way to tell is if the Smart-UPS as an LCD screen it most likely has the ability to accept firmware upgrades. If the UPS has LED front panel it cannot be upgraded.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:55 AM . Last Modified: 2024-02-14 10:36 PM
Thanks for the fast responses!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.