Hi ,
I have Smart Online UPS RT2000 (Model number SURT2000XLI) and AP9630 Network management card.
The NMC card reports the battery voltage as 54,54 volts. (13,635V/each pack)
Is it normal for Online UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:10 AM . Last Modified: 2024-03-18 12:47 AM
Hi Nihat -
I can't speak to all online UPS units, but your unit uses a temperature compensated variable rate battery charger. When the batteries are close to fully charged it switches to a trickle charge and maintains a healthy float voltage.
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:09 AM . Last Modified: 2024-03-18 12:47 AM
Hi Nihat,
This is a 48v Nominal system. 54.54V is a normal float voltage on this unit.
Please note that battery voltage does not necessarily indicate a "good" battery. Running a self test with the normal load attached will illuminate the "replace battery" indicator if the battery needs replacement.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:09 AM . Last Modified: 2024-03-18 12:47 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:09 AM . Last Modified: 2024-03-18 12:47 AM
Hi,
Thank you for feedback.
I'm not an expert on UPS's.
I have another question.
Online UPS's use float charge method or cycle charge method?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:10 AM . Last Modified: 2024-03-18 12:47 AM
Hi Nihat -
I can't speak to all online UPS units, but your unit uses a temperature compensated variable rate battery charger. When the batteries are close to fully charged it switches to a trickle charge and maintains a healthy float voltage.
Liam