Dear,
I installed a Network Management Card AP9617 the server has graceful shutdown when removed the AC power from the UPS after connected to the AC power the server is not restarting after the power restored. In the MNC configuration the option is set "restart the sever after the power restore" but after the power restored the server is not restarting automatically. We have start the server manually would you please provide me the procedure how to restart the server automatically after the power is restored.
Thanks in Advance
Regards,E
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:06 PM . Last Modified: 2024-03-14 03:44 AM
Dear,
Thank you very much for providing the information I will check with BIOS. Thank you once again.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:06 PM . Last Modified: 2024-03-14 03:44 AM
You are welcome Ahmed!!
Have a nice day!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:06 PM . Last Modified: 2024-03-14 03:44 AM
Restarting a Server is controlled by the BIOS of the Server, not our unit or our software. The APC Management software will do the shutdown in the event of extended power failure. If you want to restart your Server when power is restored, then that is a setting on the Server itself.
Follow the below K-base documents in order to set the Server to restart automatically when power is restored.
[http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1003]
[http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=948]
If you need more information on how to configure the BIOS settings, please contact your Server or BIOS manufacturer to know the exact instructions to set the BIOS settings on your particular Server.
I hope that this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:06 PM . Last Modified: 2024-03-14 03:44 AM
Dear,
Thank you very much for providing the information I will check with BIOS. Thank you once again.