I want to connect two SUVT 30 KVA UPSs in parallel-redundant configuration. Do I need to order special SBP for this, like ones we had for Silcons? If yes, please give me the part numbers. Any additional informtion about this configuration would be very helpful.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 03:48 AM . Last Modified: 2024-03-19 01:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 03:48 AM . Last Modified: 2024-03-19 01:38 AM
Hi,
You must put order SUVTOPT009S for installing 2 Smart VT 30KVA in Parallel/ Redundant configuration. This part is optional and must be installed beside of Managemant Card.
Rgds
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 03:47 AM . Last Modified: 2024-03-19 01:38 AM
i'll be investigating this for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 03:48 AM . Last Modified: 2024-03-19 01:38 AM
from what i understand, there needs to be a bypass panel of some sort. the part needs to be ordered custom so there is no part number readily available.
i'd suggest calling into three phase tech support so they can get you going in the right direction since we apparently dont have any documentation readily available with part numbers that I can post: 1-800-890-4272 opt 4 then opt 4
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 03:48 AM . Last Modified: 2024-03-19 01:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 03:48 AM . Last Modified: 2024-03-19 01:38 AM
Hi,
You must put order SUVTOPT009S for installing 2 Smart VT 30KVA in Parallel/ Redundant configuration. This part is optional and must be installed beside of Managemant Card.
Rgds