I'm assembling a system for use in Europe and as such have chosen the SURT10000RMXLI model UPS.
I have two questions regarding this model and using it temporarily in the United States during system development activities:
1) Can anyone recommend a transformer to power this UPS from USA 208/120V three phase feed?
2) What is the maximum recharging current? Equipment load on this UPS will only be about half of the rated UPS capacity, so I'm trying to determine the required sizing of transformer/cabling/breakers on the UPS input feed.
Thanks for your thoughts.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:33 PM . Last Modified: 2024-03-14 02:45 AM
No idea on the transformer, but the battery charger is 869 watts...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:33 PM . Last Modified: 2024-03-14 02:45 AM
No idea on the transformer, but the battery charger is 869 watts...