APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2024-03-12 03:21 AM
Suddenly my 4 years old SUA1500i has started signaling "battery disconnected" (dead battery led is blinking and endless intermittent beep). Before buying a new battery i would like to be sure the problem is only the battery and not the whole ups. This is the description of what happened and of the tests i performed:
1) The "battery disconnected" alarm started suddenly, previously self-test were all completed without errors
2) i tried to turn off and then on again the ups, it almost immediately went into "battery disconnected" condition
3) i tried to braindead the ups (no main power, battery cable disconnected), with the same result as the 2)
4) Pulled out the battery, checked the cable, but everything looked as normal.
5) I manually measured the battery voltage: it was 25 V
6) i noticed that the fan is not operating as usual, every 30 seconds it stops and restarts ( always at low speed)
As you can imagine i'm not convinced the problem is the battery. Why the UPS is signaling battery disconnected ? If the battery was completely dead i imagine the ups cannot sense it, but i measured 25V!!!
Any suggestions ?
The APCUPSD status show this:
APC | : 001,042,1039 |
DATE | : 2014-03-12 00:55:48 +0100 |
VERSION : 3.14.8 (16 January 2010) redhat
CABLE | : USB Cable |
MODEL | : Smart-UPS 1500 |
UPSMODE : Stand Alone
STARTTIME: 2014-03-12 00:55:45 +0100
STATUS : ONLINE NOBATT
LINEV | : 231.8 Volts |
LOADPCT : 18.8 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 69.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 60 Seconds
OUTPUTV : 231.8 Volts
SENSE | : High |
DWAKE | : -01 Seconds |
DSHUTD : 090 Seconds
LOTRANS : 208.0 Volts
HITRANS : 253.0 Volts
RETPCT : 000.0 Percent
ITEMP | : 22.0 C Internal |
ALARMDEL : Always
BATTV | : 21.3 Volts |
LINEFREQ : 50.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI : 14 days
STATFLAG : 0x03000008 Status Flag
BATTDATE : 2009-12-11
NOMOUTV : 230 Volts
NOMBATTV : 24.0 Volts
FIRMWARE : 653.18.I USB FW:7.4
APCMODEL : Smart-UPS 1500
END APC : 2014-03-12 00:55:49 +0100
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2024-03-12 03:21 AM
Suddenly my 4 years old SUA1500i has started signaling "battery disconnected" (dead battery led is blinking and endless intermittent beep). Before buying a new battery i would like to be sure the problem is only the battery and not the whole ups. This is the description of what happened and of the tests i performed:
1) The "battery disconnected" alarm started suddenly, previously self-test were all completed without errors
2) i tried to turn off and then on again the ups, it almost immediately went into "battery disconnected" condition
3) i tried to braindead the ups (no main power, battery cable disconnected), with the same result as the 2)
4) Pulled out the battery, checked the cable, but everything looked as normal.
5) I manually measured the battery voltage: it was 25 V
6) i noticed that the fan is not operating as usual, every 30 seconds it stops and restarts ( always at low speed)
As you can imagine i'm not convinced the problem is the battery. Why the UPS is signaling battery disconnected ? If the battery was completely dead i imagine the ups cannot sense it, but i measured 25V!!!
Any suggestions ?
The APCUPSD status show this:
APC | : 001,042,1039 |
DATE | : 2014-03-12 00:55:48 +0100 |
VERSION : 3.14.8 (16 January 2010) redhat
CABLE | : USB Cable |
MODEL | : Smart-UPS 1500 |
UPSMODE : Stand Alone
STARTTIME: 2014-03-12 00:55:45 +0100
STATUS : ONLINE NOBATT
LINEV | : 231.8 Volts |
LOADPCT : 18.8 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 69.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 60 Seconds
OUTPUTV : 231.8 Volts
SENSE | : High |
DWAKE | : -01 Seconds |
DSHUTD : 090 Seconds
LOTRANS : 208.0 Volts
HITRANS : 253.0 Volts
RETPCT : 000.0 Percent
ITEMP | : 22.0 C Internal |
ALARMDEL : Always
BATTV | : 21.3 Volts |
LINEFREQ : 50.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI : 14 days
STATFLAG : 0x03000008 Status Flag
BATTDATE : 2009-12-11
NOMOUTV : 230 Volts
NOMBATTV : 24.0 Volts
FIRMWARE : 653.18.I USB FW:7.4
APCMODEL : Smart-UPS 1500
END APC : 2014-03-12 00:55:49 +0100
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2024-03-12 03:21 AM
Suddenly my 4 years old SUA1500i has started signaling "battery disconnected" (dead battery led is blinking and endless intermittent beep). Before buying a new battery i would like to be sure the problem is only the battery and not the whole ups. This is the description of what happened and of the tests i performed:
1) The "battery disconnected" alarm started suddenly, previously self-test were all completed without errors
2) i tried to turn off and then on again the ups, it almost immediately went into "battery disconnected" condition
3) i tried to braindead the ups (no main power, battery cable disconnected), with the same result as the 2)
4) Pulled out the battery, checked the cable, but everything looked as normal.
5) I manually measured the battery voltage: it was 25 V
6) i noticed that the fan is not operating as usual, every 30 seconds it stops and restarts ( always at low speed)
As you can imagine i'm not convinced the problem is the battery. Why the UPS is signaling battery disconnected ? If the battery was completely dead i imagine the ups cannot sense it, but i measured 25V!!!
Any suggestions ?
The APCUPSD status show this:
APC | : 001,042,1039 |
DATE | : 2014-03-12 00:55:48 +0100 |
VERSION : 3.14.8 (16 January 2010) redhat
CABLE | : USB Cable |
MODEL | : Smart-UPS 1500 |
UPSMODE : Stand Alone
STARTTIME: 2014-03-12 00:55:45 +0100
STATUS : ONLINE NOBATT
LINEV | : 231.8 Volts |
LOADPCT : 18.8 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 69.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 60 Seconds
OUTPUTV : 231.8 Volts
SENSE | : High |
DWAKE | : -01 Seconds |
DSHUTD : 090 Seconds
LOTRANS : 208.0 Volts
HITRANS : 253.0 Volts
RETPCT : 000.0 Percent
ITEMP | : 22.0 C Internal |
ALARMDEL : Always
BATTV | : 21.3 Volts |
LINEFREQ : 50.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI : 14 days
STATFLAG : 0x03000008 Status Flag
BATTDATE : 2009-12-11
NOMOUTV : 230 Volts
NOMBATTV : 24.0 Volts
FIRMWARE : 653.18.I USB FW:7.4
APCMODEL : Smart-UPS 1500
END APC : 2014-03-12 00:55:49 +0100
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.