Please help me, i don't know extractly this problem althought i just replacement all cell.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:34 AM . Last Modified: 2024-03-13 04:10 AM
Hi Jim, how can i test exactly battery bad? please show me.
i checked by multimeter but all pin is good.
:(:(
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:34 AM . Last Modified: 2024-03-13 04:10 AM
Jim,
The error cleared at 10:35:58 "UPS: A discharged battery condition no longer exists." If you are concerned you can run a self-test to see if the new batteries are good.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:34 AM . Last Modified: 2024-03-13 04:10 AM
Problem is the led "replacement" still alert & notify "At least one faulty battery exists" appear,
i don't know how can i fix that
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:34 AM . Last Modified: 2024-03-13 04:10 AM
Jim,
You should run a self-test and if it fails you should check each battery to see if one is bad. Each batteries should have a reading of 12.5v to 14v DC if they are good. In most cases good batteries read around 13.5v DC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:34 AM . Last Modified: 2024-03-13 04:10 AM
Hi Jim, how can i test exactly battery bad? please show me.
i checked by multimeter but all pin is good.
:(:(