APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:04 AM . Last Modified: 2024-03-13 03:18 AM
Hi,
Due to a terrible mistake, I had connected 230 V on a OUT connector of my Smart Ups 1500 VA.
The UPS not go on, practically is dead.
How can I repair it?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:04 AM . Last Modified: 2024-03-13 03:18 AM
Hi,
Due to a terrible mistake, I had connected 230 V on a OUT connector of my Smart Ups 1500 VA.
The UPS not go on, practically is dead.
How can I repair it?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:04 AM . Last Modified: 2024-03-13 03:18 AM
Hi,
Due to a terrible mistake, I had connected 230 V on a OUT connector of my Smart Ups 1500 VA.
The UPS not go on, practically is dead.
How can I repair it?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.