Hello
Here is my problem with UPS. I have model SUA3000RMI2U with batteries replaced in Jun 2014. While trying to run a self-test, it failed:UPS: At least one faulty battery exists.
UPS alarm test is passed
I removed the batteries, checked UPS output voltage (55.08VDC) as well as mechanical connection and all looks fine. And since batteries are relatively new, I am not sure if they are problem or the problem is with the UPS itself. When running self test, the bad battery red LED is ON
I have another model of this UPS and it passes self-test. I have also redundancy switch installed.
What should I do next? Replace batteries again? Please advise.
Slawomir.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
Hi Slawomir,
Since you have another model of the UPS, I would swap that battery temporarily into this UPS and run a manual self test. This way you tell whether the issue is with the battery or the UPS.
Other thoughts:
- Did you purchase a genuine APC battery or purchase third party ones? If it's a genuine APC battery, there should be a white sticker with a model and serial number on it which will be helpful determining the age of the battery.
- Do you have frequent power outages or an unusual environment (ie. overly hot, etc.)?
- How long did the batteries last before you swapped them in June 2014? (knowing the UPS serial number would be helpful as well)
- Does this failed self test message occur when the UPS runs it automatically or when you run it manually?
Let me know what you find out.
- Tommy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.