APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:55 AM . Last Modified: 2024-03-12 01:31 AM
Hi,
I am wondering if there is a option to shut down servers in a specific order.
We have 6 servers. Two physical servers are connected and both servers run 2 virtual hyper-v servers.
I want to shut down the virtual servers first and then my 2 physical servers.
Is this possible and how?
UPS: Smart-UPS RT 2000 XL
Network Management Card 2
PowerChute Network Shutdown
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
Hi,
You should install PCNS on each host and then configure each host to shutdown when UPS has been on battery for x minutes or when runtime remaining is x.
Example host A starts shutdown when UPS has 30 minutes of runtime remaining. Host B starts shutdown when UPS has 25 minutes of runtime remaining.
The users guide explains this beginning onpage 20 (PDF page 23)
Note: you cannot configure the order the VMs will be powered down in.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
Hi,
You should install PCNS on each host and then configure each host to shutdown when UPS has been on battery for x minutes or when runtime remaining is x.
Example host A starts shutdown when UPS has 30 minutes of runtime remaining. Host B starts shutdown when UPS has 25 minutes of runtime remaining.
The users guide explains this beginning onpage 20 (PDF page 23)
Note: you cannot configure the order the VMs will be powered down in.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
Hi Bill,
Thanks for your respond!
This will help me to configure the UPS.
Many thanks!
Tim
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.