APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM . Last Modified: 2024-03-19 01:53 AM
Good Day,
I client is getting message saying
03/17/2017 09:05:12 UPS: An Internal communication bus fault no longer
exists.
03/17/2017 09:05:12 UPS: The main intelligence module is now in control.
03/17/2017 09:05:12 UPS: A main intelligence module fault no longer
exists.
03/17/2017 09:04:56 UPS: An Internal communication bus fault exists.
03/17/2017 09:04:56 UPS: The redundant intelligence module is in
control.
03/17/2017 09:04:56 UPS: A main intelligence module fault exists.
But the intelligence was replaced and the error continues, the IM logs states
0100D48F IM D Comm. failure on external CAN bus 17/03/21 19:48:50 000
0100A41E IM A IM has control when activated 17/03/21 19:48:50 000
0100D39E IM D Surv. error found, hearbeat is stopped 17/03/21 19:48:50 000
0100A48F IM A Comm. failure on external CAN bus 17/03/21 19:48:50 529
0100D41E IM D IM has control when activated 17/03/21 19:48:50 529
0100A39E IM A Surv. error found, hearbeat is stopped 17/03/21 19:48:50 529
0100D48F IM D Comm. failure on external CAN bus 17/03/21 11:28:46 000
0100A41E IM A IM has control when activated 17/03/21 11:28:46 000
0100D39E IM D Surv. error found, hearbeat is stopped 17/03/21 11:28:46 000
0100A48F IM A Comm. failure on external CAN bus 17/03/21 11:28:46 488
0100D41E IM D IM has control when activated 17/03/21 11:28:46 488
0100A39E IM A Surv. error found, hearbeat is stopped 17/03/21 11:28:46 488
Can anyone assist as to what is happening.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM . Last Modified: 2024-03-19 01:53 AM
Hi,
External CAN Bus:
The External CAN Bus is the communication between the MIM/RIM and any XR Battery Frames. Any Battery Monitor Boards in the XR’s would also be on this bus.
The first step in troubleshooting this problem would be to verify proper XR communication cabling. Make sure that there are two terminators installed in the circuit. The first and last ports in the chain should have a terminator (one in the UPS, one in the last XR cabinet)
In the event that there is no XR frame present, both ports on the UPS XR Comm card should be terminated.
The units are shipped with one terminator installed and a CAT5 cable connected to the second port on the XR Comm Card. Replace the cable with a terminator if no XR is present.
If all cabling is correct then you must attempt to determine which card is the cause of the alarm.
This could be the XR com card in the UPS or one of the battery cabinets, or any BMB’s in the Battery cabinets (it would not however be the BMB’s in the main UPS – that is on the internal can bus).
I also recommend you contact local support. Local support will be knowledgeable about you specific unit and any local requirements.
Contact information for local support can be found at this link.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM . Last Modified: 2024-03-19 01:53 AM
Hi,
External CAN Bus:
The External CAN Bus is the communication between the MIM/RIM and any XR Battery Frames. Any Battery Monitor Boards in the XR’s would also be on this bus.
The first step in troubleshooting this problem would be to verify proper XR communication cabling. Make sure that there are two terminators installed in the circuit. The first and last ports in the chain should have a terminator (one in the UPS, one in the last XR cabinet)
In the event that there is no XR frame present, both ports on the UPS XR Comm card should be terminated.
The units are shipped with one terminator installed and a CAT5 cable connected to the second port on the XR Comm Card. Replace the cable with a terminator if no XR is present.
If all cabling is correct then you must attempt to determine which card is the cause of the alarm.
This could be the XR com card in the UPS or one of the battery cabinets, or any BMB’s in the Battery cabinets (it would not however be the BMB’s in the main UPS – that is on the internal can bus).
I also recommend you contact local support. Local support will be knowledgeable about you specific unit and any local requirements.
Contact information for local support can be found at this link.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.