APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Time | IP address | Description |
---|---|---|
19:35:48 | 192.168.1.88 | Cannot connect to http://192.168.1.88:80 |
19:35:47 | 192.168.1.88 | Checking connection to http://192.168.1.88:80 |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Thank you very much!
It was necessary to enable HTTP for PowerChute in the NMC web interface, as written in the "useless" document.
Thank you again!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Hi,Sorry for the inconvenience. When an NMC is updated to firmware 6.8 and rebooted http is disabled. Step 14 of the mentioned FAQ discusses how to resolve the issue.
14. If the AP9630, AP9631, AP9635, AP9537SUM is running firmware 6.8.X or the NMC is a AP9640, AP9641 verify that HTTP and or HTTPS has been enable. To enable HTTP and or HTTPS open the NMC web interface and go to Configuration - Network - Web - Access. Also, verify that HTTP and or HTTPS protocol has been enable for PowerChute. To verify HTTP and or HTTPS protocol has been enable for PowerChute open the NMC web interface and go to Configuration - Shutdown. You will find the PowerChute Communication Protocol at the bottom of the page.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Thank you very much!
It was necessary to enable HTTP for PowerChute in the NMC web interface, as written in the "useless" document.
Thank you again!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.