Hello,
I am inexperienced in writing command files and I am looking create a simple file to shutdown the servers after 10 mins of power loss.
The two systems I need this file on are running;
Windows 7 Professional (64-bit) Service Pack 1 Build 7601
and
Windows Server 2008 Foundation Service Pack 2 Build 6002
Were currently running PCNS version 3.0.1 on a Smart-UPS 1500 VA (SMX1500RM2U) running firmware 6.0.6
Any help on how to correctly create this file is greatly appreciated.
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:11 AM . Last Modified: 2024-03-05 10:23 PM
Hi,
If you install PCNS on each of those server PCNS will take care of the shutdown. There is no need to write a command file. After installing PCNS just configure the event UPS: On Battery - Shut down Operating System when on battery for X.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:11 AM . Last Modified: 2024-03-05 10:23 PM
Hi,
If you install PCNS on each of those server PCNS will take care of the shutdown. There is no need to write a command file. After installing PCNS just configure the event UPS: On Battery - Shut down Operating System when on battery for X.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.