APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:43 AM . Last Modified: 2024-03-07 02:39 AM
Hi all, i need your help, is their any possibility that i can upgrade the firmware of my NMC AP9619 and the sumx_version is 120 and aos 120? coz i try to upgrade from the lates version but i got an error during process. Is their any way to upgrade the NMC? thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:43 AM . Last Modified: 2024-03-07 02:39 AM
If you have a Network Management Card (and not Network Management Card 2), then the latest version for you is 358. The 5xx firmware versions will not work. If you're upgrading the cards through FTP, you need to upgrade the AOS to version 202 first. Then 358.
Steps:
1. transfer AOS 202
2. transfer AOS 361
3. transfer SUMX 358
Or use the upgrade utility... it will automatically perform these three steps.
If you're doing it manually, the easiest way to get AOS 202 is to rename the upgrade utility from .exe to .zip and extract it out.
You can get the [SUMX v358 firmware files here|http://www.apcc.com/products/resource/include/techspec_index.cfm?base_sku=SFSUMX358].
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:43 AM . Last Modified: 2024-03-07 02:39 AM
If you have a Network Management Card (and not Network Management Card 2), then the latest version for you is 358. The 5xx firmware versions will not work. If you're upgrading the cards through FTP, you need to upgrade the AOS to version 202 first. Then 358.
Steps:
1. transfer AOS 202
2. transfer AOS 361
3. transfer SUMX 358
Or use the upgrade utility... it will automatically perform these three steps.
If you're doing it manually, the easiest way to get AOS 202 is to rename the upgrade utility from .exe to .zip and extract it out.
You can get the [SUMX v358 firmware files here|http://www.apcc.com/products/resource/include/techspec_index.cfm?base_sku=SFSUMX358].
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.