APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:28 AM . Last Modified: 2024-03-19 02:20 AM
Does anyone have a Modbus register map for the Symmetra MW (2006 vintage, if it matters) and ISX 60 kW PDU?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:28 AM . Last Modified: 2024-03-19 02:20 AM
Hi Ben,
I don't work with 3PH units, but I asked someone on that team to help out. He said it would depend on the firmware level installed on the display which set of Modbus data points you would need for the MW. I have attached the most recent for 3.5.9.112. The ISX60kw doesn't support modbus natively, but you may have luck converting snmp to modbus using other resources. This would use our standard mib file for snmp (see this link).
If you don't have the latest fw revision listed earlier, I would advise calling into your local technical support and discussing options with them, but let me know if there is anything else you need.
Thanks,
Tommy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:28 AM . Last Modified: 2024-03-19 02:19 AM
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.