I entered the server room today to find that one of the smartcells in my Matrix 5000 smells, is hot, and has deformed batteries!!
It was the last cell in the series.
I quickly placed ups in bypass, and removed the cell, then placed the unit back online.
BOTH smartcells were professionally rebuilt and factory reset, and had been fine since then, but in the last 48 hours, this happened.
Anyone ever heard of this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
I forgot - is this a SMARTCELL or SMARTCELL-XR? SMARTCELLs are not supposed to be opened up and repaired so if that's the case then
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
I entered the server room today to find that one of the smartcells in my Matrix 5000 smells, is hot, and has deformed batteries!!
It was the last cell in the series.
I quickly placed ups in bypass, and removed the cell, then placed the unit back online.
BOTH smartcells were professionally rebuilt and factory reset, and had been fine since then, but in the last 48 hours, this happened.
Anyone ever heard of this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
Where were these batteries from? It sounds like batteries from the vendor that rebuilt and reset the unit?
You could have measured the voltage on this SmartCell or it could have just been a bad cell. I was thinking potentially a charger issue so if the voltage was super high, then that would be a concern or the bad cell depending on the quality of the battery itself.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
The batteries were from BatteriesPlus and the brand is "Werker".
Two cells were rebuilt at the same time, and these two were the only two attached to the unit.
Only one of the cells had the problem and it was the last one in the series.
The other is fine.
This APC unit is the same one that had the problem listed in the following post:
Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.
According to the logs, the unit started to alert that looked like this:
08/18/2013 | 16:01:12 | UPS: An external battery pack was installed. |
08/18/2013 | 16:00:57 | UPS: An external battery pack was removed.. |
08/18/2013 | 16:00:10 | UPS: Restored communication with the battery packs. |
08/18/2013 | 15:59:40 | UPS: Lost communication with the battery packs. |
08/18/2013 | 15:58:38 | UPS: An external battery pack was installed. |
08/18/2013 | 15:58:23 | UPS: An external battery pack was removed.. |
08/18/2013 | 15:57:37 | UPS: Restored communication with the battery packs. |
08/18/2013 | 15:57:06 | UPS: Lost communication with the battery packs. |
08/18/2013 | 15:55:49 | UPS: Restored communication with the battery packs. |
08/18/2013 | 15:55:34 | UPS: Lost communication with the battery packs. |
08/18/2013 | 15:55:03 | UPS: An external battery pack was installed. |
08/18/2013 | 15:54:48 | UPS: An external battery pack was removed.. |
08/18/2013 | 15:53:00 | UPS: Restored communication with the battery packs. |
08/18/2013 | 15:52:45 | UPS: Lost communication with the battery packs. |
08/18/2013 | 15:51:59 | UPS: Restored communication with the battery packs. |
Just horrible crap happening to this cell for some reason.
Any thoughts are appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
Those types of alarms could occur with low battery voltage. If there was a bad cell, it could've dipped.
If you just have the "good" Smartcell connected, do you see this type of behavior?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
Correct, everything is working as expected/is normal with the remaining smart smartcell connected.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
That's right, as I first stated, this is not an XR unit. I know they are not supposed to be rebuilt. but never had this issue after having done several of these.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
OK - missed that in the title. Or maybe I remembered but someone else asked me and I forgot
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
Is that SmartCell that was just re-worked under warranty? Beyond checking the charging voltage to make sure the UPS did not damage good batteries, not much we can do as far as I know.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:40 AM . Last Modified: 2024-03-12 11:10 PM
I forgot - is this a SMARTCELL or SMARTCELL-XR? SMARTCELLs are not supposed to be opened up and repaired so if that's the case then
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.