I tried to upgrade my AP7920
Model Number: | AP7920 |
Serial Number: | ZA1447024983 |
Hardware Revision: | B2 |
Manufacture Date: | 11/24/2014 |
MAC Address: | 00 C0 B7 8A 22 BE |
Management Uptime: | 0 Days 0 Hours 23 Minutes |
Name: | rpdu |
Version: | v3.9.2 |
Date: | 07/07/2016 |
Time: | 10:40:30 |
Name: | aos |
Version: | v3.9.2 |
Date: | 07/06/2016 |
Time: | 15:12:05 |
With the latest firmware using apc_hw05_aos656_rpdu2g656_bootmon108.exe
But I get the following error in the log:
Ping Test 12/13/18 15:36:57
-----------------
Starting Upgrade 12/13/18 15:37:10
-----------------
[12/13/18 15:37:10] 192.168.0.217: Pinging (via ICMP) device
[12/13/18 15:37:10] 192.168.0.217: Device connection passed
[12/13/18 15:37:11] 192.168.0.217: Testing FTP Log-in
[12/13/18 15:37:14] 192.168.0.217: FTP Log-in passed
[12/13/18 15:37:16] 192.168.0.217: Saving data file
[12/13/18 15:37:29] 192.168.0.217: ERROR --> Incompatible HW
[12/13/18 15:37:29] 192.168.0.217: Incompatible HW: apc_hw02_aos_392.bin
192.168.0.217: Incompatible HW:
Please do not tell me I cannot upgrade this device!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:27 PM
Hi,
Your PDU is already at the latest version (3.9.2). Version 6 firmware is only supported on AP7XXXB models or AP8XXX series models which are different hardware platforms and the error you're seeing is legitimate - incompatible hardware.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:27 PM
Hi,
Your PDU is already at the latest version (3.9.2). Version 6 firmware is only supported on AP7XXXB models or AP8XXX series models which are different hardware platforms and the error you're seeing is legitimate - incompatible hardware.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.