Hello all,
Does anyone know how many BTU (1) 8kVA Symmetra LX + (2) Symmetra LX XR 9-pod Cabinets gives off?
Also, how much would (1) SUM3000RMXL2U + (9) SUM48XLBP2U give off?
Total load is 4600W.
Let me know your thoughts, thank you!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:38 PM . Last Modified: 2024-03-06 11:53 PM
Thank you for the quick reply. Much appreciated!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:38 PM . Last Modified: 2024-03-06 11:53 PM
Hello,
The Symmetra LX 8K while online will give off 3485.0BTU/hr. The SUM3000RMXL2U while online will give off 300.0BTU/hr. The thermal dissipation of the extended battery cabinets while online is negligible for both units.
Thanks!
Caylin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:38 PM . Last Modified: 2024-03-06 11:53 PM
Thank you for the quick reply. Much appreciated!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.