Hi
I need guidance on calibrating UPS. I have onsite three types of UPS
Smart UPs 750
Smart-UPS 3000
Symmetra LX 16000
I want to calibrate all 3 and do this from the Network card/Web interface. My question is this. I can see from other discussions mention of a 30% load. However I think this might apply to doing the calibration manually and on older UPS. Do I need to have a 30%+ load on these types when doing it via the webpage. If so why and where is the APC guidance on this (as I have yet to find it).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:48 AM
For any UPS, there are certain conditions that need to be met in order for the UPS to accept a command to run a runtime calibration to ensure the calibration is as accurate as possible and worthwhile. Make sure you only do a runtime calibration 1-2 times a year or after you replace the batteries.
In general, you can find some of this information in the knowledge base and within the product user's guides.
Hope that helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:48 AM
For any UPS, there are certain conditions that need to be met in order for the UPS to accept a command to run a runtime calibration to ensure the calibration is as accurate as possible and worthwhile. Make sure you only do a runtime calibration 1-2 times a year or after you replace the batteries.
In general, you can find some of this information in the knowledge base and within the product user's guides.
Hope that helps.