APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-25 09:39 AM
Firmware update is Failing on Model SMART-UPS X1000
Any one have any idea how to fix this?
Update pending: ID1031UPS 15.0
Last Update Result
Refused due to UPS in Invalid State
UPS Firmware
Current Version
ID1031UPS 02.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-28 07:13 PM
Hi @KevC
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. Apologies for the issue that you've experienced.
Will you be able to share the serial number of the UPS as well as the full UPS firmware like the UPS and CBL firmware versions? I would have to check if there is a specific firmware that we need to upload first on the UPS prior to moving to the latest.
Early versions of the SMX units (serials prior to AS1037) would need to upgrade their CBL to version 2.x before upgrading it to the latest. Also, when you were doing the firmware upgrade, was the UPS turned off?
Below are the articles that you can use to guide you with the different options/ways to upgrade the firmware of the UPS.
I hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.