APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:48 AM . Last Modified: 2024-03-19 12:33 AM
We have a Galaxy 3000 with two external battery cabinets. Occationaly, while transfering to battery power due to power outage, the battery breaker trips. This results in a total shutdown of the ups. On subsequent power up, there is no entry in event log of what caused the problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:48 AM . Last Modified: 2024-03-19 12:33 AM
I consulted with a 3 phase support technician. This sounds like dead batteries - we'd recommend you get the batteries in the cabinet tested and then possibly look into replacing based on the test results.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:48 AM . Last Modified: 2024-03-19 12:33 AM
I consulted with a 3 phase support technician. This sounds like dead batteries - we'd recommend you get the batteries in the cabinet tested and then possibly look into replacing based on the test results.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.