Hello. The ACSC100 along with most DX cooling units are plugged directly to utility power (no UPS). This is due to the start up draw of the compressor which can over most UPS's unless the UPS is way over sized. To answer the question, plugging the ACSC100 directly to utility power is fine.
Thank you