APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:39 AM . Last Modified: 2024-03-17 11:54 PM
So I have connected my BR1500G to a Square Wave Output Inverter and the UPS is switching to main and battery whenever the Inverter is going to Backup mode but I was told by APC Service team that if I use a pure sinewave output inverter it will just work fine
So will it work fine if I get a pure sine wave output inverter?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:39 AM . Last Modified: 2024-03-17 11:54 PM
One other thing to consider when powering a UPS via an inverter or generator is that when the UPS powers on, it will pull current from the inverter / generator which may cause the inverter / generator to reduce its voltage and /or frequency to compensate for the load. This can cause the UPS to transfer to battery due to "unacceptable input power". That lets the inverter / generator recover, and when the UPS senses that it will transfer off battery and the cycle will repeat over and over. This generally means that you need a substantially higher wattage inverter / generator than you would think, based on the UPS nameplate rating.
I think there used to be a knowledge base article on this, but that was decades ago and those have been re-organized multiple times since then.
Edit: I found it (or something similar) - FA158891. It looks like FA158842 and FA157508 may also apply.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:39 AM . Last Modified: 2024-03-17 11:54 PM
Hi Sandipan,
The UPS is designed to monitor the quality of the sine-wave it is being provided and switch to battery power when deemed necessary. The Square-wave output of the Inverter will definitely not be accepted by the UPS. As long as the inverter you are using outputs a Pure Sine-wave with RMS voltage within the correct 120vac/60hz range and minimal harmonic distortion, the UPS should accept the power.
Secret Squirrel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:39 AM . Last Modified: 2024-03-17 11:54 PM
One other thing to consider when powering a UPS via an inverter or generator is that when the UPS powers on, it will pull current from the inverter / generator which may cause the inverter / generator to reduce its voltage and /or frequency to compensate for the load. This can cause the UPS to transfer to battery due to "unacceptable input power". That lets the inverter / generator recover, and when the UPS senses that it will transfer off battery and the cycle will repeat over and over. This generally means that you need a substantially higher wattage inverter / generator than you would think, based on the UPS nameplate rating.
I think there used to be a knowledge base article on this, but that was decades ago and those have been re-organized multiple times since then.
Edit: I found it (or something similar) - FA158891. It looks like FA158842 and FA157508 may also apply.