APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:48 AM . Last Modified: 2024-03-15 04:20 AM
Smart-UPS RT 5000 XL
I'm getting ready to do some major hardware upgrades in my server room. I noticed that the LED indicators for the battery charge level were blinking. Decided to plug a network cable in and check out the GUI. Ignore the date as it is way off. Here is what I am seeing.
02/03/2020 | 08:04:18 | device | Web user 'device' logged in from X.X.X.X |
02/03/2020 | 07:58:10 | System | File transfer failed. |
02/03/2020 | 07:57:57 | System | Network service started. System IP is X.X.X.X from DHCP server X.X.X.X with 691190 second lease. |
02/03/2020 | 04:31:39 | Device | UPS: A low battery condition no longer exists. |
02/03/2020 | 04:31:39 | Device | UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. |
02/03/2020 | 04:31:37 | Device | UPS: No longer on battery power. |
02/03/2020 | 04:31:36 | Device | UPS: A discharged battery condition no longer exists. |
02/03/2020 | 04:31:36 | Device | UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon. |
02/03/2020 | 04:31:36 | Device | UPS: On battery power in response to rapid change of input. |
02/03/2020 | 04:31:32 | Device | UPS: A low battery condition no longer exists. |
02/03/2020 | 04:31:32 | Device | UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. |
02/03/2020 | 04:31:32 | Device | UPS: No longer on battery power. |
02/03/2020 | 04:31:31 | Device | UPS: A discharged battery condition no longer exists. |
02/03/2020 | 04:31:31 | Device | UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon. |
02/03/2020 | 04:31:30 | Device | UPS: On battery power in response to rapid change of input. |
02/03/2020 | 04:31:04 | Device | UPS: A low battery condition no longer exists. |
02/03/2020 | 04:31:04 | Device | UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. |
02/03/2020 | 04:31:03 | Device | UPS: No longer on battery power. |
02/03/2020 | 04:31:02 | Device | UPS: A discharged battery condition no longer exists. |
02/03/2020 | 04:31:02 | Device | UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon. |
02/03/2020 | 04:31:02 | Device | UPS: On battery power in response to rapid change of input. |
The input voltage seems to range from 211.9VAC to 213.8VAC.
UPS Output | |||
Output Voltage: | 208.5 VAC | @ 60.0 Hz | |
Load Current: | 5.3 Amps | ||
Output VA: | 28.1 % | ||
Output Watts: | 28.9 % |
Can anyone help shed some light on my problem? My battery runtime shows 24seconds.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:48 AM . Last Modified: 2024-03-15 04:20 AM
Thanks for giving the information iMessage for PC
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:48 AM . Last Modified: 2024-03-15 04:20 AM
Hi Shae,
It doesn't look good but I would recommend contacting your local APC by Schneider support team and having them look over the debugs, they should do it even if it's old and out of warranty but they won't be able to replace any parts for you.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:48 AM . Last Modified: 2024-03-15 04:20 AM
Thanks for giving the information iMessage for PC
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.