APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 2024-03-07 12:31 AM
We are relocating our servers. We have 3 APC SUA2200RM2u (120V).
What power outlet and rating do we need for these?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 2024-03-07 12:31 AM
Hi,
The SUA2200RM2U requires 20 amp 120 volt input. The plug type is NEMA 5-20. Here is a link to the data sheet http://datasheet.octopart.com/SUA2200RM2U-APC-datasheet-11971591.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:14 PM . Last Modified: 2024-03-07 12:31 AM
Hi,
The SUA2200RM2U requires 20 amp 120 volt input. The plug type is NEMA 5-20. Here is a link to the data sheet http://datasheet.octopart.com/SUA2200RM2U-APC-datasheet-11971591.pdf
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.