Hello i have a question:
Exist a set of commands line for autoshutdown a APC SMART-UPS SRT 6000VA when the battery is low?(without programs or tools) If is possible can you link or post the right command?
Thanks and sorry if is the wrong section.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:37 PM . Last Modified: 2024-03-14 04:15 AM
Hello,
Your UPS comes with an embedded UPS Network Management Card. This management card offers a command line interface via serial connection, telnet, and SSH. You can control the UPS through there.
Another "command line" type option is SNMP v1 or v3 which the management card also supports. The embedded card is a variant of AP9631 so you can review the documentation here for the command line. v6.2.0 firmware is the latest available and I'd recommend it for the best support of the SRT product line.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9631&tab=documentation
From there, you can see the detail on how to configure the network management card and what commands are available.
With SNMP, you'd need the APC PowerNet MIB which can be downloaded from here http://www.apc.com/tools/download/index.cfm and once that is compiled and loaded, you can also control the UPS that way.
Hope that helps get you started.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:37 PM . Last Modified: 2024-03-14 04:15 AM
Hello,
Your UPS comes with an embedded UPS Network Management Card. This management card offers a command line interface via serial connection, telnet, and SSH. You can control the UPS through there.
Another "command line" type option is SNMP v1 or v3 which the management card also supports. The embedded card is a variant of AP9631 so you can review the documentation here for the command line. v6.2.0 firmware is the latest available and I'd recommend it for the best support of the SRT product line.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9631&tab=documentation
From there, you can see the detail on how to configure the network management card and what commands are available.
With SNMP, you'd need the APC PowerNet MIB which can be downloaded from here http://www.apc.com/tools/download/index.cfm and once that is compiled and loaded, you can also control the UPS that way.
Hope that helps get you started.