We are going to perform a firmware upgrade on an AP8841 PDU. Is there any risk of losing power during the upgrade and reboot?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:25 AM . Last Modified: 2024-03-18 11:18 PM
Hi Scott,
Only the NMC will reboot not the whole PDU, there should be no impact on the load.
-Gavan