APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hi,
I have an AP7721 and I noticed that the +12V power supply has failed however the -12V is still on an o.k. status. What is the reccommened course of action? My building is taking down one leg of power for maint next weekend, will this PS failure prevent the switch from trasnferring to the other leg? Or should I replace the unit immediately? Any advice? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
honestly i am not sure. i will look into it. i know on switched rack PDUs for example we have a primary and secondary power supply and if both fail, it will usually cause the PDU to drop the load since the power supplies power the relays that control whether the outlet is on or off.
i'll see what i can find out
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
generally a power supply fault requires a unit replacement but it might be good for you to post the event.txt first to verify this is not a false alarm due to something else. you can follow these instructions to get event.txt -> http://nam-en.apc.com/app/answers/detail/a_id/9321
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
honestly i am not sure. i will look into it. i know on switched rack PDUs for example we have a primary and secondary power supply and if both fail, it will usually cause the PDU to drop the load since the power supplies power the relays that control whether the outlet is on or off.
i'll see what i can find out
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.