Hello,
I just bought a 1400 UPS (with no batterties). I also purchased the batteries, but not quite sure how to connect them together. Can someone help?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
If yours is an North American (US/Can) model the battery pack voltage is 24 VDC. Two series strings of 12 Volt 9.0 Ah connected in parallel. You can get away with 7.2 Ah cells in a pinch...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
This is not something that APC helps users with since we sell the Replacement Battery Cartridge (RBC) modules as pre-wired parts with all required connectors. If someone else here wants to help, then that is fine but you'll be doing it at your own risk.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
Please clarify - did you buy the raw battery cells ? If so, you may not have the necessary fuse(s) and prewired spade terminal wiring and possibly Anderson connector to mate with the UPS's battery connections.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
Batman - I have all the cables, just not sure if I should wire the batteries as 24V or 48V for the 1400 model.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
If yours is an North American (US/Can) model the battery pack voltage is 24 VDC. Two series strings of 12 Volt 9.0 Ah connected in parallel. You can get away with 7.2 Ah cells in a pinch...