Hi everyone, I've been looking around for answers but no one is able to help me so far.
We have a rack at a datacenter with a 208V/60 amp circuit coming into a 208V/60 AMP PDU and I was wondering if we lower the circuit to let say 208V/30 amp or 120/30 amp do I need to change the PDU to a 208V/30 or 120/30 as to match the amperage on the circuit?
I guess my question is if the PDU has to always match the amperage and volts of the circuit?
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:21 AM . Last Modified: 2024-03-18 03:36 AM
Hi everyone, I've been looking around for answers but no one is able to help me so far.
We have a rack at a datacenter with a 208V/60 amp circuit coming into a 208V/60 AMP PDU and I was wondering if we lower the circuit to let say 208V/30 amp or 120/30 amp do I need to change the PDU to a 208V/30 or 120/30 as to match the amperage on the circuit?
I guess my question is if the PDU has to always match the amperage and volts of the circuit?
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:20 AM . Last Modified: 2024-03-18 03:36 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:20 AM . Last Modified: 2024-03-18 03:36 AM
If cost is an issue then why would you consider buying anything if you already have as I see it.
PDU w/60A CB -------60A cordset-------- Rackmount 60A PDU.
You only loose capacity by replacing the 60A pdu with a 30A pdu. If you don't need the 60A capacity only use 30A of it. It doesn't hurt anything to keep it at a low load level.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:21 AM . Last Modified: 2024-03-18 03:36 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:21 AM . Last Modified: 2024-03-18 03:36 AM
I suspect you have your rack hosted at a co-location centre and they're charging you for the size of the service to your rack regardless of the actual consumption. This is an all too common tactic of many hosting sites, but, it's money for them; they charge you to install the service, then they charge a monthly rental.
If you can confirm your load is under 24 Amps (the code limit for a 30 Amp service), then you could downgrade the service to 30 Amps. The electrical service will be protected from overload by the 30 Amp breaker. While you're at it, set the warning thresholds on the PDU to correspond to the 30 Amp Service; 20 Amps for near overload, 24 Amps for overload (for example). This is not a preferred solution as it introduces the possibility of overloading the service and nuisance tripping of the breaker.
The better option would be to use a 30 Amp PDU on a 30 Amp Service.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:21 AM . Last Modified: 2024-03-18 03:36 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:21 AM . Last Modified: 2024-03-18 03:36 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:21 AM . Last Modified: 2024-03-18 03:36 AM
Hi everyone, I've been looking around for answers but no one is able to help me so far.
We have a rack at a datacenter with a 208V/60 amp circuit coming into a 208V/60 AMP PDU and I was wondering if we lower the circuit to let say 208V/30 amp or 120/30 amp do I need to change the PDU to a 208V/30 or 120/30 as to match the amperage on the circuit?
I guess my question is if the PDU has to always match the amperage and volts of the circuit?
Thanks in advance