Is there a model number matrix available for the Smart-UPS VD series?
I'm using the internet sizing configurator.
For the same connected load but changine my run-times, the number of add-on battery cabinets change (as I would expect it to).
However, the base UPS Chassis also changes the 10th digit of the model number.
For the base UPS Chassis, my two configurations are:
SUVTR20KF{color:#ff0000}3{color}B5S for a run-time of 1 hour (plus 1 x SUVTBXR6B6S Battery Cabinets)
SUVTR20KF{color:#ff0000}4{color}B5S for a run-time of 2 hours (plus 2 x SUVTBXR6B6S Battery Cabinets)
What does the 10th digit (3 vs 4 in my example) signify??
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:28 AM . Last Modified: 2024-03-19 12:48 AM
SUVTR20KF3B5S and SUVTR20KF4B5S are essentially the same UPS.
SUVTR20KF3B5S has 3 battery modules out of a possible 5
SUVTR20KF4B5S has 4 battery modules out of a possible 5
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:28 AM . Last Modified: 2024-03-19 12:48 AM
SUVTR20KF3B5S and SUVTR20KF4B5S are essentially the same UPS.
SUVTR20KF3B5S has 3 battery modules out of a possible 5
SUVTR20KF4B5S has 4 battery modules out of a possible 5