Hello all,
We have a galaxy 3000 ups that after a restart return charger fault and the battery cb goes off after 5 to 10 seconds of the startup.
The batteries are fully charged, each one reads between 13.3 and 13.5, the whole group reads 320v.
Any idea I appreciate.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM . Last Modified: 2024-03-19 01:53 AM
Luis,
I asked our Galaxy support team and they replied
Most likely he has an open battery or connection in his battery string.
They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM . Last Modified: 2024-03-19 01:53 AM
Luis,
I asked our Galaxy support team and they replied
Most likely he has an open battery or connection in his battery string.
They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM . Last Modified: 2024-03-19 01:53 AM
You need to measure the voltage of each battery separately, necessarily with a small load of 2-5 watts