APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:14 AM . Last Modified: 2024-03-07 11:22 PM
I have a Matrix 5000 with an AP9606 snmp/web card installed.
In the web console I changed the UPS Name setting located in Configuration | General Settings section from the default "UPS_IDEN" to "TRD LEFT".
Since then I have lost access to the Matrix 5000's configuration settings in both web and telnet sessions.
In the web console now, I don't even see the Matrix 5000 menu item on the left side of the page.
In telnet, I get a message "A ups was found that is not supported by this application."
This new UPS name is stored in the EU. When I traverse the menus I see the new name "TRD LEFT" stored as the UPS ID in the diagnostic menu.
I am convinced that this problem was caused by this name change and more specifically because there is a space in the new name.
Does anybody know of a way to reset this name in the EU?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:14 AM . Last Modified: 2024-03-07 11:21 PM
Just to confirm, you're running SUMX firmware on this 9606 that can be obtained here:
ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v326b/
use SUMX326A.bin and AOS326B.bin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:14 AM . Last Modified: 2024-03-07 11:21 PM
Just to confirm, you're running SUMX firmware on this 9606 that can be obtained here:
ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v326b/
use SUMX326A.bin and AOS326B.bin