5414 DI Module - 12V Option?

Solved
bp21901
Ensign
Ensign
0 Likes
2
111

5414 DI Module - 12V Option?

With the consolidation of the I/O modules recently and the 5403-12 going away with the suggested replacement 5414-24, will / can the 5414 work with 12V DI's? 

 

A customer has had a 5414 in for testing for a while and says it has 12/24 on it and the data sheet seems to indicate there is a 12V option that is factory config'ed.  


Accepted Solutions
Joel_Weder
Commander Commander
Commander
0 Likes
1
105

Re: 5414 DI Module - 12V Option?

Hello Bob,

 

Yes, the 5414 will work with 12 volt inputs. I know the description in the price list is a bit confusing as it just mentions 24v. But in the user manual, the specification called "Input Logic - Hi Level" states that the transition threshold is typically 5.5 volts. So no issue at all with any voltage between 12 and 24v.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

2 Replies 2
Joel_Weder
Commander Commander
Commander
0 Likes
1
106

Re: 5414 DI Module - 12V Option?

Hello Bob,

 

Yes, the 5414 will work with 12 volt inputs. I know the description in the price list is a bit confusing as it just mentions 24v. But in the user manual, the specification called "Input Logic - Hi Level" states that the transition threshold is typically 5.5 volts. So no issue at all with any voltage between 12 and 24v.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
bp21901
Ensign
Ensign
0 Likes
0
102

Re: 5414 DI Module - 12V Option?

Thanks for the info Joel...Besides the '-24' the other thing that had me asking is the data sheet notes Factory Configurable on the 12/24V range so I thought it might be a board level switch I missed seeing in the manual.