Power Distribution and Digital
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-03 12:08 PM
How does adjusting the trip on a circuit breaker affect the marked 80% continuous operation rating? See CEC C22.1-18 8-104 6). Ie. is the trip adjustment a percentage of the 80% continuous rating?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-07 05:25 AM
Hello,
In Schneider Electric / Square D range of adjustable circuit breaker there is no link between the setting of overload protection "Ir'" and the 80% or 100% rating capability of the circuit-breaker.
Selecting 80% standard rating or 100% rating is more a question of enclosure design due to thermal dissipation for continuous load, rather than a setting question that is linked to the ampacity of the protected circuit.
Masterpact circuit breakers and PowerPact M,P, R frames are designed for continuous operation at 100% of their current rating, and the setting of Ir is given in % of "In" the rated current of the trip unit.
PowerPact B, H,J, L ranges are offering "80% rated" or "100% rated" references. Both will have the same trip units with overload setting in Amps. A 80% rated should be adjusted up to 80% of the rating when used with a continuous load but can be ajdusted up to 100% with non continous load.
Does it answer your question ?
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-07 05:25 AM
Hello,
In Schneider Electric / Square D range of adjustable circuit breaker there is no link between the setting of overload protection "Ir'" and the 80% or 100% rating capability of the circuit-breaker.
Selecting 80% standard rating or 100% rating is more a question of enclosure design due to thermal dissipation for continuous load, rather than a setting question that is linked to the ampacity of the protected circuit.
Masterpact circuit breakers and PowerPact M,P, R frames are designed for continuous operation at 100% of their current rating, and the setting of Ir is given in % of "In" the rated current of the trip unit.
PowerPact B, H,J, L ranges are offering "80% rated" or "100% rated" references. Both will have the same trip units with overload setting in Amps. A 80% rated should be adjusted up to 80% of the rating when used with a continuous load but can be ajdusted up to 100% with non continous load.
Does it answer your question ?
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-07 11:58 AM
Hello Mathieu
Thank you for taking the time to respond to my question. This is crystal clear.
Best regards,
Brian
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.