Posted: 2021-03-23 10:50 PM . Last Modified: 2021-03-23 10:51 PM
Native "Health Timeout" and "Last Value" settings in Concept/Unity/Control Expert IO Scanner allows inter-PLC communication with fallback to "0" in event of comms loss (built-in-watchdog)
I've now transitioned to Global Data (Multicast Publisher/Subscriber inter-PLC comms). Do I need to build my own watchdog bit into the Global Data DDTs or is there a similar "fallback to 0" feature?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-28 04:45 PM
I would strongly recommend installing a watchdog as the first or last register in the data transfer from each PLC. I would also ensure that each participating PLC publishes at least a watchdog.