BMECRA31210 Service Port

Is it possible to connect Modbus TCP device to BMECRA31210 Service Port?

Tags (1)

Accepted Solutions
AlastairF
Lieutenant Lieutenant
Lieutenant
0 Likes
4
609

Re: BMECRA31210 Service Port

Definitely yes.

Outlined in this manual in a number of places.

This Service port is not restricted to MBTCP communications.

M580 Standalone System Planning Guide 

See Answer In Context

Tags (1)
5 Replies 5
AlastairF
Lieutenant Lieutenant
Lieutenant
0 Likes
4
610

Re: BMECRA31210 Service Port

Definitely yes.

Outlined in this manual in a number of places.

This Service port is not restricted to MBTCP communications.

M580 Standalone System Planning Guide 

Tags (1)
aleksei_bontsev
Crewman
Crewman
0 Likes
3
524

Re: BMECRA31210 Service Port

How to add Modbus TCP device to BMECRA31210 service port?

Does Modbus TCP device is added in the DTM Browser?
Does Modbus TCP device is added to Distributed Bus, Remote Bus or BME_NOC0301?
How to configure it?
Could you please help?
Tags (1)
dhemsing
Cadet
0 Likes
2
522

Re: BMECRA31210 Service Port

What type of device are you trying to add? 

Tags (1)
aleksei_bontsev
Crewman
Crewman
0 Likes
1
520

Re: BMECRA31210 Service Port

PLC - Carel pCO3 with Modbus TCP extension card.

Tags (1)
FrancisBreysach
Crewman Crewman
Crewman
0 Likes
0
515

Re: BMECRA31210 Service Port

Hello,

 

Modbus TCP devices connected to the Service port of BME CRA  are added in the DTM Browser.

It is the scanner of the CPU who is used, no BME NOC required.

This Scanner can Manage 61 Devices for CPU xx40 Modele.

The MBTCP Device must be adressed with the same IP Adresse as the CPU IP  Adress A.

To add a device, open the DTM Browser, right clic on the CPU and ADD a device.

 

BR

 