IEEEFloat format modbus slave

Solved
huseyinb
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
88

IEEEFloat format modbus slave

Hi,

 

I need floating point value for 3rd modbus master, As mentioned on page 362 of the ion reference document, this format is available.

 

image.png

 

but i connected to 7650 and format list not included float point

 

image.png

Hüseyin Bayram
Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: IEEEFloat format modbus slave

Hello @huseyinb 

 

You are correct that the ION7650 meter does not support IEEE float formats in the modbus slave modules. Below is a copy from the ION Reference document
"NOTE: The registers and settings available in this module depend on the device or node you are configuring, as well as its firmware and template versions. Not all registers or settings are available on all devices or the Virtual Processor, and labels may vary."

 

If you were to look at the modbus slave module of the PM8000/ION7400/ION9000, you would see the option to select IEEE Float. This is why the option is listed in ION Reference.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
1 Reply 1
Charles_Murison
Picard Picard
Picard

Re: IEEEFloat format modbus slave

Hello @huseyinb 

 

You are correct that the ION7650 meter does not support IEEE float formats in the modbus slave modules. Below is a copy from the ION Reference document
"NOTE: The registers and settings available in this module depend on the device or node you are configuring, as well as its firmware and template versions. Not all registers or settings are available on all devices or the Virtual Processor, and labels may vary."

 

If you were to look at the modbus slave module of the PM8000/ION7400/ION9000, you would see the option to select IEEE Float. This is why the option is listed in ION Reference.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities