Hello,
I have a question about wiring method of PM8000.
There is only one wiring method described in the installation manual of PM8000 for 3CT.
But there are two wiring method described n the installation manual of ION9000 for 3CT.
(Please refer to the attached document.)
Could I use the wiring method of ION9000 for PM8000(3CT, 4W-WYE) ?
Regards,
Okada
Link copied. Please paste this link to share this article on your social media post.
Hello @Tomohiro-Okada,
The wiring diagram you are referring to is included in the PM8000 user guide under residual current
https://www.productinfo.schneider-electric.com/pm8000/594169a446e0fb0001570843/PM8000%20user%20manua...
Installation and commissioning -> Installation -> Residual current measurement
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Tomohiro-Okada ,
this section of the Community is for Power Monitoring Expert topics. I suggest you post this question in Metering & Power Quality section to get the answer.
Link copied. Please paste this link to share this article on your social media post.
Hello @Tomohiro-Okada,
The wiring diagram you are referring to is included in the PM8000 user guide under residual current
https://www.productinfo.schneider-electric.com/pm8000/594169a446e0fb0001570843/PM8000%20user%20manua...
Installation and commissioning -> Installation -> Residual current measurement
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Charles_Murison,
Thank you for your prompt reply!
I checked PM8000 user manual(Residual current measurement)
and understand about wiring method for PM8000.
Regards,
Okada