Industry Automation and Control Forum
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-03 08:56 PM
Hello,
I am using a expansion module TM172E28R on a TM172PDG42R controller with Machine Expert - HVAC software.
I have setup my controller and software exactly like in this video from Schneider: https://www.youtube.com/watch?v=pyJA31G2yQk&list=PLa7UGrWOTyjlgMo0lD4eVCV0zFQYxbLoa&index=7
I have setup up the controller as Can-Bus Master address 125 and the TM172E as slave address 1, also the dip switches are set (4-5-6 all off), the dip switcdh number one is on and is the EOL resistor.
I have also added a 120 Ohm resistor on the Can-Bus terminal from the M172P.
Somehow i cannot get the Master running with the slave running.
The sys variables for the CANbus communication is all zero.
I also have a input from the expansion module in my watch and its always false (voltmeter shows me 24VDC).
Is there anything what I can try else? Or is there a setting i need to set that is not in the manual?
The Firmware of TM172P is "596.10".
Any help is appreciated. Thank you.
Regards,
Michael
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-09 01:48 AM
Did you made a download all? Only in that case the CONNEC.PAR which is used for the communication will be downloaded. On the expansion is near the CAN Port a LED. Is this LED flashing? What is the status of sysCANopenNodeStauts[3]?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-09 01:48 AM
Did you made a download all? Only in that case the CONNEC.PAR which is used for the communication will be downloaded. On the expansion is near the CAN Port a LED. Is this LED flashing? What is the status of sysCANopenNodeStauts[3]?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-15 02:57 PM
Thanks for your help, that LED was not flashing, it was a wire mistake on the bus.
It works now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-26 12:25 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-14 08:33 AM
any updates for this issue because i have the same problem ??? @Mick0275
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.