I'd like to map modbus RTU addresses to Profibus DP using a LUFP7 Gateway.
1. Can I map custom modbus-RS485 registers to custom Profibus addresses with LUFP7?
2. Where can ABC-LUFP Config Tool programming software be downloaded from, and is it compatible with modern operating systems? (2009 documentation referred to)
Link copied. Please paste this link to share this article on your social media post.
Hi Scott,
The LUFP7 is a very old device (I'm even not sure whether it is still available or not) and I don't think that the software (ABC-LUF config tool) will run on new OS (maybe in compatibility mode). For this I normally run it on a Windows 7/XP VM.
It is possible to use it for custom devices that are communicating over RS485 with Modbus-RTU (see attached document that we created many years ago).
But you must be aware that one is very limited with this gateway: 128 16-bit registers max. in total for all connected slaves and each request has to be programmed. You must also be very careful with timings
Just a suggestion from me: Use Anybus X-Gateway instead. The advantage is, that it can be "programmed" over integrated web pages and if applicable in your system, it can also support Modbus-TCP with Profibus DP which means, that you can connect your devices to a simple gateway like the Link150 and communicate in parallel with the Anybus X-Gateway to the devices over the Link150. So your system stays open that the connected devices can communicate with a Modbus system like PME on one side and to a Profibus system on the other side (which is not the case with a LUFP7 where you will end on Profibus DP). Here is a link to the HMS page where you can select the gateway with the networks/protocols (1 and 2) that shall be supported:
https://www.anybus.com/products/gateway-index
BR
Daniel
Link copied. Please paste this link to share this article on your social media post.
Hi Scott,
The LUFP7 is a very old device (I'm even not sure whether it is still available or not) and I don't think that the software (ABC-LUF config tool) will run on new OS (maybe in compatibility mode). For this I normally run it on a Windows 7/XP VM.
It is possible to use it for custom devices that are communicating over RS485 with Modbus-RTU (see attached document that we created many years ago).
But you must be aware that one is very limited with this gateway: 128 16-bit registers max. in total for all connected slaves and each request has to be programmed. You must also be very careful with timings
Just a suggestion from me: Use Anybus X-Gateway instead. The advantage is, that it can be "programmed" over integrated web pages and if applicable in your system, it can also support Modbus-TCP with Profibus DP which means, that you can connect your devices to a simple gateway like the Link150 and communicate in parallel with the Anybus X-Gateway to the devices over the Link150. So your system stays open that the connected devices can communicate with a Modbus system like PME on one side and to a Profibus system on the other side (which is not the case with a LUFP7 where you will end on Profibus DP). Here is a link to the HMS page where you can select the gateway with the networks/protocols (1 and 2) that shall be supported:
https://www.anybus.com/products/gateway-index
BR
Daniel