Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
61 | |
46 | |
28 | |
27 |
Link copied. Please paste this link to share this article on your social media post.
Looking at https://www.se.com/ww/en/faqs/FA285178/
, it appears that there is several types of IFM devices for similarly named breaker models.
Regarding device type selection in Schneider gateways (Com'X / PAS server):
1. In a Com'X, Is a Compact NS is an A/E/H/P com'x model type selected for NSX breakers with Micrologic A/E/H/P trip units?
2. Is there a similar file to the above link detailing supported devices for Ecostruxure Panel Servers (e.g. PAS600 / PAS800)? If so, please provide it.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @swil ,
FA285178 is not up to date. Better look at the matrix file delivered with the Com'X FW package.
Compact NS has not the same Trip Units as Compact NSX.
If you integrate a Compact NSX please select:
Compact NS is sharing the same Micrologic trip units as MasterPact. Try to declare your Compact NS as Masterpact A/P/E/H device type.
For the Panel Server, the list of compatible devices is described on the release notes:
Link copied. Please paste this link to share this article on your social media post.
Hello swill
As you mention in your post, there are two generation of IFM gateway (gen1: TRV00210 and gen2: LV434000)
hereunder the answer to the Question2 of your post about compatibility of IFM with Panel Server.
Even if the two generation of IFM are supported by the Panel Server , You must check that the association of IFM+ the downstream circuit breaker is supported (not only the IFM interface!)
To do this, please refer to the the release note of the Panel Server (PAS600 : ref DOCA0178EN-05 / PAS800: ref DOCA0248EN-02) § Supported devices/Modbus serial Devices
Note also that release note are updated for each new fw version... so take care to use the last one
BR
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.