Geo SCADA: Alarm Acknowledge Using Pick Action VBScript Function

PicardEarlGrey
Crewman
Crewman

Geo SCADA: Alarm Acknowledge Using Pick Action VBScript Function

Hi everyone!

 

I want to accept alarms from an alarm list using a VBScript function. I am not able to get the "cookie" value when selecting the row

 

'Assume for this purpose that strAlarmSource is fullname

 

     strAlarmSource = Mimic.Layers(strLayerName).Item(strListName).CurrentRowSource 

     objAlarm = Server.FindObject(strAlarmSource)

     objAlarm.Interface.Accept

 

and then when using the method "objAlarm.Interface.Accept" it would accept all active alarms on that object. Is there any way to select a row in an alarm list and get a reference to the Alarm Instance and not the object or "Alarm Source".

 

Thank you in advance!

1 Reply 1
BevanWeiss
Spock
Spock
0 Likes
0
235

Re: Geo SCADA: Alarm Acknowledge Using Pick Action VBScript Function

I think it's a little complicated there.

  strAlarmSource = Mimic.Layers(strLayerName).Item(strListName).CurrentRowSource

  objAlarm = Server.FindObject(strAlarmSource)

  objAlarm.Interface.Accept

 

The objAlarm item there is really the Alarm Object (CAlarmObject)

2022-05-26 14_25_44-GeoSCADA Expert 2021 Win2016 - VMware Workstation.png

 

And hence the Accept will 'Acknowledges all alarms associated with the object'

 

So somewhat painfully, you'd ideally want to access the CAlarm itself instead of the Alarm Object.