APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:19 PM . Last Modified: 2024-02-14 10:10 PM
Hello,
We have Smart-UPS VT 40 kVA w/4 Batt Mod Exp to 4, int Maint Bypass, Parallel Capable SUVTP40KH4B4S, PS0813240713, Firmware Revision: 912.0405.I.
There are two critical mistakes:
In bypass in response to an internal hardware fault.
A power module fault exists.
Can we try to reboot to get rid of them?
Bellow – our adventures…
01.12.2015 |
07:53:13 |
UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance. |
01.12.2015 |
07:53:12 |
UPS: Restored the local network management interface-to-UPS communication. |
01.12.2015 |
07:52:47 |
System: Network service started. System IP is 10.4.142.230 from manually configured settings. |
01.12.2015 |
07:52:47 |
System: Warmstart. |
01.12.2015 |
07:51:49 |
UPS: The output power is now turned on. |
01.12.2015 |
07:51:48 |
UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance. |
01.12.2015 |
07:48:50 |
UPS: An internal mechanical bypass no longer exists. |
01.12.2015 |
07:48:30 |
UPS: The output power is turned off. |
01.12.2015 |
07:48:29 |
UPS: The external Switch Gear Q003 has opened. |
01.12.2015 |
07:47:38 |
System: NTP update failure. |
01.12.2015 |
07:47:28 |
UPS: The output power is now turned on. |
01.12.2015 |
07:47:28 |
UPS: An internal mechanical bypass exists. |
01.12.2015 |
07:47:28 |
UPS: The external Switch Gear Q003 has closed. |
01.12.2015 |
07:46:04 |
UPS: An internal mechanical bypass no longer exists. |
01.12.2015 |
07:46:03 |
UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. |
01.12.2015 |
07:45:47 |
UPS: The external Switch Gear Q003 has opened. |
01.12.2015 |
07:45:41 |
UPS: The output power is turned off. |
01.12.2015 |
07:45:28 |
UPS: An internal mechanical bypass exists. |
01.12.2015 |
07:45:28 |
UPS: The external Switch Gear Q003 has closed. |
01.12.2015 |
07:40:42 |
UPS: An input voltage or frequency problem prevents switching to bypass mode. |
02.12.2015 |
01:53:51 |
UPS: In bypass in response to an internal hardware fault. |
02.12.2015 |
01:53:51 |
UPS: A power module fault exists. |
02.12.2015 |
00:15:39 |
UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. |
02.12.2015 |
00:15:18 |
UPS: An input voltage or frequency problem prevents switching to bypass mode. |
02.12.2015 |
00:15:17 |
UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. |
02.12.2015 |
00:14:57 |
UPS: An input voltage or frequency problem prevents switching to bypass mode. |
02.12.2015 |
00:14:57 |
UPS: In bypass in response to an internal hardware fault. |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:19 PM . Last Modified: 2024-02-14 02:20 AM
Bill, thanks a lot for your reply.
We have done restart of the device. And “raw status” now is OK. No mistakes at all!
M States = 07 04 04
00000000 00000000
00000000 02
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:19 PM . Last Modified: 2024-01-29 11:37 PM
Hello Vladimir,
I suggest first contacting the technical support group for your region:
http://www.apc.com/site/support/index.cfm/contact-information/ (choose your county with the drop down menu, so it will give you the approriate tech support phone
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 11:19 PM . Last Modified: 2024-02-14 02:20 AM
Bill, thanks a lot for your reply.
We have done restart of the device. And “raw status” now is OK. No mistakes at all!
M States = 07 04 04
00000000 00000000
00000000 02
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.