Posted: 2022-04-30 11:37 AM . Last Modified: 2022-04-30 11:43 AM
Hello,
I have a SRC1KUXI 800W online UPS. It has recently started tripping off when main goes off. I have checked the two SMF batteries attached and they showed 13.20V and 13.23V respectively. A self-test on the UPS comes out ok.
Here is a video after it has tripped,
https://i.imgur.com/4t4AaDS.mp4
The host is running apcupsd. This is what i get from a running system,
$apcaccess
APC : 001,038,0930
DATE : 2022-04-30 23:56:31 +0530
HOSTNAME : nas
VERSION : 3.14.14 (31 May 2016) unknown
UPSNAME : pfsense
CABLE : Ethernet Link
DRIVER : NETWORK UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2022-04-30 23:27:28 +0530
MASTERUPD: 2022-04-30 23:56:31 +0530
MASTER : x.x.x.x:3551
MODEL : SRC1KUXI
STATUS : ONLINE
LINEV : 236.1 Volts
LOADPCT : 55.0 Percent
BCHARGE : 95.0 Percent
TIMELEFT : 175.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
OUTPUTV : 236.2 Volts
LOTRANS : 160.0 Volts
HITRANS : 265.0 Volts
RETPCT : 60.0 Percent
ITEMP : 40.0 C
BATTV : 28.8 Volts
LINEFREQ : 50.0 Hz
LASTXFER : Automatic or explicit self test
NUMXFERS : 0
TONBATT : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x05000408
BATTDATE : 2018-09-19
NOMOUTV : 230 Volts
NOMBATTV : 24.0 Volts
END APC : 2022-04-30 23:57:27 +0530
The UPS is only loaded 55%. Any idea what could be the issue?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-26 02:54 AM
Hi @rajil.s_apc
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. Apologies for the late revert on this post of yours.
If you are still experiencing this issue with your UPS, may I know if we can remove the load attached to the UPS and then unplug the unit from the power source?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.