Hello!
When input voltage drops under 208VAC AVR kicks in to compensate for low input voltage.
Everything seems to be working fine. But what is bothering me is , when AVR starts to compensate for low input voltage and switches to batteries, Powerchute shows that output voltage goes as high 240-247VAC.
Screen - http://foto.inbox.lv/anarchy91/26-01-2008/AVR.jpg
Shouldnt it be around 220-225VAC ? Can my pc be damaged with so high output voltages ?
Thanks.
UPS model is - SUA1500I
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:40 PM . Last Modified: Tuesday
It's less then 10% higher than the nominal 230V. Don't worry.
Message was edited by: rau
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:40 PM . Last Modified: Tuesday
I don't know why it outputs 243Volts, but I can assure you it won't demage your PSU. Your PSU while working @ 230V as it's nominal input voltage, it can compensate for fluctuations between 180-260V. If your PSU is one with Active PFC don't even bother if the input voltage is 100V or 265V. It'll work fine at anything between 90-260V. AVRs in my opinion are something not necessary for modern PSUs. Switch mode PSU can cope with a relatively wide voltage range and those witch Active PFC can work with anything you give them.
Message was edited by: rau
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:40 PM . Last Modified: Tuesday
VES,
Your SUA1500I is an international UPS which has a nominal input and output voltage of 230VAC. Keep in mind this is one hot leg, one neutral and one ground. 208VAC is domestic power of 2 hots and a ground. Therefore if the input voltage is too low, AVR should boost it around 12% or so, if not a little more, or even force it on battery which will go back to 230VAC +/-5%
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:40 PM . Last Modified: Tuesday
Still 247VAC seems a bit high to me 😉
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:40 PM . Last Modified: Tuesday
It's less then 10% higher than the nominal 230V. Don't worry.