I have a 5-6 year old APC XS 1300G BackUPS device that seems to switch to battery even when there isn't a event that occurs. The fan and display kick on, then off, and does this one or two more times. This occurs maybe every 5-6 hours.
It's certainly possible it's the battery, but I don't want to replace the batter until I can confirm that is the exact reason.
This occurs if there is and is not any devices powered-on or off. I've tried multiple outlets across two floors of my home. At this time, the load on the UPS unit is around 5-6%
I've turned off the green or eco mode as well. quickpayportal
There are 4 other UPSes in this home that do not have this problem.
I've also ran the battery down entirely to see if it just needed a full cycle, same issues once fully charged.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:50 PM . Last Modified: 1 month ago
On 3/24/2021 7:08 PM, Oliver said:I have a 5-6 year old APC XS 1300G BackUPS device that seems to switch to battery even when there isn't a event that occurs. The fan and display kick on, then off, and does this one or two more times. This occurs maybe every 5-6 hours.
It's certainly possible it's the battery, but I don't want to replace the batter until I can confirm that is the exact reason.
This occurs if there is and is not any devices powered-on or off. I've tried multiple outlets across two floors of my home. At this time, the load on the UPS unit is around 5-6%
I've turned off the green or eco mode as well . PrepaidGiftBalance quickpayportal
There are 4 other UPSes in this home that do not have this problem.
I've also ran the battery down entirely to see if it just needed a full cycle, same issues once fully charged.
I suspect it is a side-effect of the Automatic Voltage Regulation (AVR) feature. I've found that adjusting the voltage sensitivity to make it less sensitive to small fluctuations make it less likely to kick on at "random" times.
In my case, I traced the triggering event to the HVAC blower motor, swapped the breaker for the circuit serving the UPS to the other side of the breaker panel and the issue went away entirely.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:50 PM . Last Modified: 1 month ago
On 3/24/2021 7:08 PM, Oliver said:I have a 5-6 year old APC XS 1300G BackUPS device that seems to switch to battery even when there isn't a event that occurs. The fan and display kick on, then off, and does this one or two more times. This occurs maybe every 5-6 hours.
It's certainly possible it's the battery, but I don't want to replace the batter until I can confirm that is the exact reason.
This occurs if there is and is not any devices powered-on or off. I've tried multiple outlets across two floors of my home. At this time, the load on the UPS unit is around 5-6%
I've turned off the green or eco mode as well . PrepaidGiftBalance quickpayportal
There are 4 other UPSes in this home that do not have this problem.
I've also ran the battery down entirely to see if it just needed a full cycle, same issues once fully charged.
I suspect it is a side-effect of the Automatic Voltage Regulation (AVR) feature. I've found that adjusting the voltage sensitivity to make it less sensitive to small fluctuations make it less likely to kick on at "random" times.
In my case, I traced the triggering event to the HVAC blower motor, swapped the breaker for the circuit serving the UPS to the other side of the breaker panel and the issue went away entirely.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.