Recently I replaced the batteries of my ups SURT20K with the same old batteries but the ups still fault (replace the battery)and the run time still the same i tried to cut the power on ups to see the real time of discharging but its the same on screen
what i can do to solve this ??
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:26 AM . Last Modified: 2024-03-17 11:18 PM
Hi Ahmed
If you still have the fault light showing after replacing the batteries then a self test should clear that.
As for the runtime not being correct I reccommend running the runtime calibration to give you the new runtime.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:26 AM . Last Modified: 2024-03-17 11:18 PM
Hi Ahmed
If you still have the fault light showing after replacing the batteries then a self test should clear that.
As for the runtime not being correct I reccommend running the runtime calibration to give you the new runtime.
Regards
Matt