APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
Dear all
We purchased SURT 8000VA UPS.
We want to know that UPS have the reverse current protection for preventing a failed UPS from discharging the battery.
If yes, we want to receive the relevant document such as the technical manual mentioned as the reverse current protection.
We also want to know that UPS have the earth fault protection or alarm.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
hello,
i am not familiar with ELB and NFB so I asked someone else and we definitely do not have an ELB in there so I guess it'd be NFB?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
hello,
the units themselves do not have earth fault protection built in if I am understanding you correctly. they have an input circuit breaker which protects against over current.
they also have a site wiring fault alarm that can come up - noted here-> http://www.apc.com/support/index?page=content&id=FA158817
there is no reverse current protection. the UPS has a manual and automatic bypass but it is electronic. also, in most situations, if the SURT goes to bypass, it will discharge over time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
Thank you for your reply.
We have one question again
We want to know that the input circuit breaker is ELB or NFB.
Thanks & Best regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
hello,
i am not familiar with ELB and NFB so I asked someone else and we definitely do not have an ELB in there so I guess it'd be NFB?